版主: 51FPGA
分享到:
共1条 1/1 1
全自动洗衣机控制器
    [您是本帖的第1894位阅读者]
redzzb
我是GG
高级会员
最后登陆时间:2010-06-02 14:46:07
直达楼层
1# 发表于 2009-08-25 22:29:58
简易的全自动洗衣机控制器
library ieee;
use ieee.std_logic_1164.all;
use ieee.std_logic_unsigned.all;
entity XiYiJi is
              port(
                     clk_50M        :in std_logic;
                     k_select :in std_logic;
                     k_run_stop     :in std_logic;
                     led_state  :out std_logic_vector(3 downto 0);---zhishi 11 ge zhuang tai
                     hex0              :out std_logic_vector(7 downto 0);
                     hex1              :out std_logic_vector(7 downto 0);
                     hex2              :out std_logic_vector(7 downto 0);
                     hex3              :out std_logic_vector(7 downto 0);
                     ctrl_danxi       :out std_logic;
                     ctrl_danpiao:out std_logic;
                     ctrl_dantuo :out std_logic);
end XiYiJi;
architecture state_machine1 of XiYiJi is
type state_type is (s_wt_idle,s_wt_dx,s_wt_dp,s_wt_dt,s_wt_pt,s_wt_xpt,s_dx,s_dp,s_dt,s_pt,s_xpt);
signal present_state,next_state:state_type;
signal a1,a2,a3:integer range 0 to 9;
signal a4:integer range 0 to 9;
signal clk_10ms:std_logic;
signal clk_10ms_v:std_logic_vector(1 downto 0);
signal time_up : std_logic;
signal k1_v,k2_v:std_logic_vector( 5 downto  0  );
signal from_idle:std_logic;
signal state_unfinish:std_logic;
begin
caiyang:process(clk_50M,k_select,k_run_stop)
       begin
              if rising_edge(clk_10ms) then
                     k1_v(5)<=k1_v(4);          --用于消抖
                     k1_v(4)<=k1_v(3);
                     k1_v(3)<=k1_v(2);
                     k1_v(2)<=k1_v(1);
                     k1_v(1)<=k1_v(0);
                     k1_v(0)<=k_select;
                     k2_v(5)<=k2_v(4);
                     k2_v(4)<=k2_v(3);
                     k2_v(3)<=k2_v(2);
                     k2_v(2)<=k2_v(1);
                     k2_v(1)<=k2_v(0);
                     k2_v(0)<=k_run_stop;
              end if ;
       end process;
state_transfer:process(clk_10ms,present_state,next_state,k1_v,k2_v)
       begin
              if rising_edge(clk_10ms)then
                     if present_state=s_wt_idle then
                            from_idle<='1';----zan ting hou  ji shi xian shi panduan
                            if k1_v ="00011"then
                                   next_state<=s_wt_dx;
                            end if ;
                     elsif present_state=s_wt_dx then
                            if k1_v="00011"then
                                   next_state<=s_wt_dp;
                            end if;
                            if k2_v="00011"then
                                   next_state<=s_dx;
                            end if ;
                     elsif present_state=s_wt_dp then
                            if k1_v="00011"then
                                   next_state<=s_wt_dt;
                            elsif k2_v="00011"then
                                          next_state<=s_dp;
                            end if ;
                     elsif present_state =s_wt_dt then
                            if k1_v="00011"then
                                   next_state<=s_wt_pt;
                                   next_state<=s_dt;
                            end if ;
                     elsif present_state=s_wt_pt then
                            if k1_v="00011"then
                                   next_state<=s_wt_xpt;
                                   next_state<=s_pt;
                            end if ;
                     elsif present_state=s_wt_xpt then
                            if k1_v="00011"then
                                   next_state<=s_wt_idle;
                                   next_state<=s_xpt;
                            end if ;
                     elsif present_state=s_dx then
                            from_idle<='0';
                            if time_up='1'then
                                   state_unfinish <='0';
                            end if;
                            if k2_v="00011" then
                                   state_unfinish <='1';
                            end if ;
                     elsif present_state=s_dp then
                            from_idle<='0';
                            if time_up='1'then
                            end if;
                            if k2_v="00011"then
                            end if ;
                     elsif present_state=s_dt then
                            from_idle<='0';
                            if time_up='1'then
                            end if;
                            if k2_v="00011"then
                            end if ;
                     elsif present_state=s_pt then
                            from_idle<='0';
                            if time_up='1'then
                            end if;
                            if k2_v="00011"then
                            end if ;
                     elsif present_state=s_xpt then
                      from_idle<='0';
                            if time_up='1'then
                            end if;
                            if k2_v="00011"then
                            end if ;
                  end if;
              end if;
       end process;
fenpin_1ms:process(clk_50M)
variable clk_div:integer range 0 to 25;--0000;
begin
       if rising_edge(clk_50M)then
              clk_div:=clk_div+1;
              if clk_div=25 then--0000
                     clk_10ms<=not clk_10ms;
                     clk_div:=0;
           end if;
        end if;
end process;
caiyang1:process(clk_50M,clk_10ms)-----caiyang yongyi xiaochu shijian yanchi
       begin
              if rising_edge(clk_50M) then
                     clk_10ms_v(1)<=clk_10ms_v(0);
                     clk_10ms_v(0)<=clk_10ms;
              end if;
       end process;
state_register:process(clk_50M)
       begin
                     present_state<=next_state;
              end if;
       end process;
zhuangtaichuli:process(clk_50M,clk_10ms_v,present_state,time_up)
begin
              case present_state is
                     when s_wt_idle =>
                            a4<=8;a3<=8;a2<=8;a1<=8;
                            led_state <="1111";
                            ctrl_danxi<='0';---lv deng yun xing zhishi
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                     when s_wt_dx =>
--                   if state_unfinish='1'then
                            if from_idle='1'or time_up='1'then
                                   a4<=2;a3<=0;a2<=0;a1<=0;
                            end if ;
                            led_state <="0001";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                     when s_wt_dp =>
                                   a4<=1;a3<=5;a2<=0;a1<=0;
                            end if;
                            led_state <="0010";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                     when s_wt_dt =>
                                   a4<=1;a3<=0;a2<=0;a1<=0;
                            end if ;
                            led_state <="0011";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                     when s_wt_pt =>
                                   a4<=3;a3<=5;a2<=0;a1<=0;
                            end if;
                            led_state <="0100";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                     when s_wt_xpt =>
                                   a4<=4;a3<=5;a2<=0;a1<=0;
                            end if ;
                            led_state <="0101";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                     when s_dx =>
                            led_state <="0110";
                            ctrl_danxi<='1';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
                            if clk_10ms_v="01" then----------weihe jiu neng xiaochushijianyanchi
--                          if rising_edge(clk_10ms)then
                                   a1<=a1-1;
                                   if a1=0 then
                                          a2<=a2-1;a1<=9;
                                          if a2=0 then
                                                 a3<=a3-1;a2<=9;
                                                 if a3=0 then
                                                        a4<=a4-1;a3<=9;
                                                        if a4=0 and a3=0 and a2=0 and a1=0 then
                                                        time_up<='1';
                                                        a4<=0;a3<=0;a2<=0;a1<=0;
                                                        else time_up<='0';
                                                 end if;
                                          end if;
                                   end if;
                            end if;
                     end if;
                  when s_dp =>
                            led_state <="0111";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='1';
                            ctrl_dantuo<='0';
                                   a1<=a1-1;
                                   if a1=0 then
                                          a2<=a2-1;a1<=9;
                                          if a2=0 then
                                                 a3<=a3-1;a2<=9;
                                                 if a3=0 then
                                                        a4<=a4-1;a3<=9;
                                                        time_up<='1';
                                                        else time_up<='0';
                                                 end if;
                                          end if;
                                   end if;
                            end if;
                     end if;
                     when s_dt =>
                            led_state <="1000";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='1';
                                   a1<=a1-1;
                                   if a1=0 then
                                          a2<=a2-1;a1<=9;
                                          if a2=0 then
                                                 a3<=a3-1;a2<=9;
                                                 if a3=0 then
                                                        a4<=a4-1;a3<=9;
                                                        time_up<='1';
                                                        else time_up<='0';
                                                 end if;
                                          end if;
                                   end if;
                            end if;
                     end if;
                     when s_pt =>
                            led_state <="1001";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='1';
                            ctrl_dantuo<='1';
                                   a1<=a1-1;
                                   if a1=0 then
                                          a2<=a2-1;a1<=9;
                                          if a2=0 then
                                                 a3<=a3-1;a2<=9;
                                                 if a3=0 then
                                                        a4<=a4-1;a3<=9;
                                                        time_up<='1';
                                                        else time_up<='0';
                                                 end if;
                                          end if;
                                   end if;
                            end if;
                     end if;
                     when s_xpt =>
                            led_state <="1010";
                            ctrl_danxi<='1';
                            ctrl_danpiao<='1';
                            ctrl_dantuo<='1';
                                   a1<=a1-1;
                                   if a1=0 then
                                          a2<=a2-1;a1<=9;
                                          if a2=0 then
                                                 a3<=a3-1;a2<=9;
                                                 if a3=0 then
                                                        a4<=a4-1;a3<=9;
                                                        time_up<='1';
                                                        else time_up<='0';
                                                 end if;
                                          end if;
                                   end if;
                            end if;
                     end if;
                     when others =>
                            led_state <="1111";
                            ctrl_danxi<='0';
                            ctrl_danpiao<='0';
                            ctrl_dantuo<='0';
              end case;
       end if;
end process;
a1yimaxianshi:process(clk_50M,a1)
begin
              case a1 is
                     when 0=>
                     hex0<="11000000";
                     when 1=>
                     hex0<="11111001";
                     when 2=>
                     hex0<="10100100";
                     when 3=>
                     hex0<="10110000";
                     when 4=>
                     hex0<="10011001";
                     when 5=>
                     hex0<="10010010";
                     when 6=>
                     hex0<="10000010";
                     when 7=>
                     hex0<="11111000";
                     when 8=>
                     hex0<="10000000";
                     when others=>
                     hex0<="10010000";
              end case;
       end if;
end process;
a2yimaxianshi:process(clk_50M,a2)
begin
              case a2 is
                     when 0=>
                     hex1<="11000000";
                     when 1=>
                     hex1<="11111001";
                     when 2=>
                     hex1<="10100100";
                     when 3=>
                     hex1<="10110000";
                     when 4=>
                     hex1<="10011001";
                     when 5=>
                     hex1<="10010010";
                     when 6=>
                     hex1<="10000010";
                     when 7=>
                     hex1<="11111000";
                     when 8=>
                     hex1<="10000000";
                     when others=>
                     hex1<="10010000";
              end case;
       end if;
end process;
a3yimaxianshi:process(clk_50M,a3)
begin
              case a3 is
                     when 0=>
                     hex2<="11000000";
                     when 1=>
                     hex2<="11111001";
                     when 2=>
                     hex2<="10100100";
                     when 3=>
                     hex2<="10110000";
                     when 4=>
                     hex2<="10011001";
                     when 5=>
                     hex2<="10010010";
                     when 6=>
                     hex2<="10000010";
                     when 7=>
                     hex2<="11111000";
                     when 8=>
                     hex2<="10000000";
                     when others=>
                     hex2<="10010000";
              end case;
       end if;
end process;
a4yimaxianshi:process(clk_50M,a4)
begin
              case a4 is
                     when 0=>
                     hex3<="11000000";
                     when 1=>
                     hex3<="11111001";
                     when 2=>
                     hex3<="10100100";
                     when 3=>
                     hex3<="10110000";
                     when 4=>
                     hex3<="10011001";
                     when 5=>
                     hex3<="10010010";
                     when 6=>
                     hex3<="10000010";
                     when 7=>
                     hex3<="11111000";
                     when 8=>
                     hex3<="10000000";
                     when others=>
                     hex3<="10010000";
              end case;
       end if;
end process;
end state_machine1;
关键词:全自动    洗衣机    控制器    logic    state    d
fffff。
共1条 1/1 1
快速回复主题
  • 匿名不能发帖!请先 [ 登陆 注册 ]